Which size copper THWN conductor is required for a tap from a 400A, 480V, 3-Phase feeder to serve a 150A load using the 10' tap rule?

Prepare for Load Calculations Test with comprehensive questions on feeders and services. Engage with multiple choice questions, hints, and explanations. Gear up for success!

To determine the appropriate size of the copper THWN conductor for a tap from a 400A, 480V, 3-Phase feeder to serve a 150A load, applying the 10' tap rule is crucial. The 10' tap rule allows for a smaller conductor size when the tap is less than 10 feet in length, and the load is less than 10% of the feeder's rating.

In this case, since the load is 150A, we should first check if it is less than 10% of the feeder’s capacity. The feeder is rated at 400A, and 10% of that is 40A. Therefore, since 150A is significantly larger than this threshold, the tap needs to be sized appropriately based on the load rather than solely on the 10% rule.

According to the National Electrical Code (NEC) guidelines, for a 150A load, the appropriate conductor size must be based on the ampacity of the conductor. For copper THWN insulation, 150A typically requires No. 1 AWG copper wire when adhering to the standard calculations for conductors rated for continuous loads (taking into account the temperature rating and installation conditions).

In this context