A 240-volt feeder supplying twelve 120-volt, 30A shore power receptacles requires a minimum ampacity of _____ amperes if the demand factor is 80%?

Prepare for Load Calculations Test with comprehensive questions on feeders and services. Engage with multiple choice questions, hints, and explanations. Gear up for success!

To determine the minimum ampacity required for a feeder supplying multiple receptacles, you must first consider the demand factor and the total load. In this scenario, you have twelve 120-volt, 30A shore power receptacles.

  1. Calculate the total load: Each receptacle can draw a maximum of 30 amperes at 120 volts. For twelve receptacles, the maximum possible load would be:

[

\text{Total load} = 12 , \text{receptacles} \times 30 , \text{A} = 360 , \text{A}

]

  1. Apply the demand factor: The demand factor is typically a consideration that accounts for the fact that not all devices will be in use simultaneously. In this case, you're given a demand factor of 80%, which means you need to calculate 80% of the total load:

[

\text{Adjusted load} = 360 , \text{A} \times 0.80 = 288 , \text{A}

]

  1. Adjust for feeder capacity: Since this is a 240-volt feeder supplying 120-